    0 votes

    Please explain the difference between MCB, MCCB, ELCB and RCCB and their respective applications.

    Also, I have heard about RCBO and RCD. What are they? Is RCBO and RCD similar in principle?

    #661 Reply
    votes +1
    Profile photo of Kiran Daware
    Kiran Daware
    Keymaster
    26 votes
    Points: 300
    Query Resolver

    Difference between MCB, MCCB, ELCB, RCCB

    MCB (Miniature Circuit Breaker)

    MCB is commonly used in low voltage electrical network, such as homes, for overcurrent protection. MCB automatically disconnects the network in abnormal conditions such as overload or faults. MCBs are generally used for operating currents below 63 Amps. In some cases, MCBs can be used up to 100 Amps also.

    MCCB (Moulded Case Circuit Breaker)

    MCCBs also offer protection from short circuits and overcurrents (overloads), but they operate for higher current levels than MCBs. MCCBs are commonly used for operating current between 63 Amps to 800 Amps. They are also available for operating currents as low as 25 A and as high as 1000A.

    ELCB (Earth Leakage Circuit Breaker)

    As the name suggests, an ELCB is used to detect a current flowing through the earth (ground wire). If ground current exceeding few milliamps is dected, the ELCB trips (disconnects) the circuit from the supply. ELCB is also known as Ground Fault Circuit Interrupter (GFCI)

    RCCB (Residual Current Circuit Breaker)

    RCCB trips the circuit when any mismatch between phase current and neutral current is detected. That means, RCCB operates for earth faults (when the phase wires gets in contact with the ground). Most widely used RCCBs are 30 mA and 100 mA device, which means they will trip the circuit if the difference between phase current and neutral current is more than 30 mA and 100 mA respectively. Most of the RCCBs are designed to trip the circuit within 30 milliseconds when a mismatch is detected. RCCBs are extremely effective for preventing electric shock hazards. For example, if someone touches the phase wire accidently, a part of current will flow through the human body and hence causing mismatch between phase current and neutral current. In this case, the RCCB will trip the circuit almost instantly and thus preventing the shock hazard. RCCBs are also called as Residual Current Device (RCD).

    RCBO (Residual current Circuit Breaker with Overcurrent protection)

    RCBO is basically a combination of MCB an RCCB in one device. RCBO provides overload protection as well as earth fault protection.

    #1257 Reply

    mohamed
    0 votes

    MCBs are miniature circuit breakers with optimum protection facilities of overcurrent only.These are manufactured for fault level of up to 10KA only with operating current range of 0.5 to 63 Amps (the ranges are fixed), single,double and three pole verson.These are used for smaller loads -electronic circuits,house wiring etc.

    MCCBs are Moulded case Circuit breakers,with protection facilities of overcurrent, earth fault. it has a variable range of 50% to 100% operating current.They can be wired for remote as well as local operation both.They are manufactured for fault levels of 16KA to 50KA and operating current range of 25A to 630Amps.They are used for aplication related with larger power flow requirement