Centre tapped transformer

Forums Common electrical queries Centre tapped transformer

This topic contains 1 reply, has 2 voices, and was last updated by Profile photo of Kiran Daware Kiran Daware 8 months, 3 weeks ago.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #1183 Reply
    Profile photo of srinivas
    srinivas
    Participant
    0 votes
    Points: 14

    In centre tapped transformer (12v-0-12v) when i measured voltage between phase to neutral that is 12v,and line to line 24v but line to line voltage was to be zero volts (voltage were 180°opposite to each other between line to neutral) why voltage between line to line not zero?

    #1190 Reply
    Profile photo of Kiran Daware
    Kiran Daware
    Keymaster
    26 votes
    Points: 300
    Query Resolver

    Consider the center tapping point as O,  the upper terminal as A and the lower terminal as B. Now, in a center tapped transformer Voa is 180 degrees out of phase with Vob. But, the Vao and Vob are in phase with each other. So, the voltage between terminals A and B is additive.

    Learn in more details at the following link, where you will understand the addition of AC voltages that are not in same phase and even learn about polarity of AC voltages.  https://www.ibiblio.org/kuphaldt/electricCircuits/AC/AC_2.html

     